What is an isolated ground receptacle ...


Recommended Posts

  • Members

The mechanical mounting yoke is seperate from the ground pin. They must be used in an isolated ground wiring configuration per the code and UL listing because incorrect wiring can lead to dangerous conditions.

 

Ground pin and yoke must be connected together always, and in an isolated ground installation this is done by a seperate green wire ground to the ground pin IN ADDITION to bonding the yoke to the conduit ground system. This gives better control over ground noise PROVIDED the isolated ground system is properly designed. There is a lot of detail necessary in this kind of application and I see mistakes all the time that make the system ineffective or less effective.

 

It's also used with power isolation transformer installations, where the ground pin goes to the derived ground and the yoke goes to the conduit system ground.

 

Better off passing on them because you will not be able to use them in the correct configuration.