01-31-2013 12:17 PM
theshow wrote:
------Anyway, as far as the Peavey distro being 80 amps, that is the spec that the site gives. I know it says it has 6 available 20 amp circuits (3 - 20 amp circuits per leg as you pointed out) but according to their site, the Peavey distro is only rated for 80 amps of TOTAL load. Unless I'm reading something wrong there.
I can tell you as I designed it but as a former employee I am NOT speaking for Peavey nor for my current employer.
UL has an odd rule that derates the plug that is mounted on the cable to 40A ... even though it is a 50A plug. Once that plug is mounted to a cable that "cable assembly" can only be rated for 40A. Go figure???
If the box were supplied without a cable it would have carried a 50A UL rating. So each leg can distribute that "rated" 40A (if you get my drift) across 3 20A breakers to that max.
"Capable" and "rated" have different meanings 
01-31-2013 01:07 PM - edited 01-31-2013 02:15 PM
theshow wrote:Is your 400 ft. SO feeder cable code approved?
My rig's been inspected a few times by L&I and local county electrical inspectors... I've never been red-tagged or written a correction notice.
theshow wrote:I'm only going off of the calculator chart online but at 400', your cables would be too small to accomodate the load drop over that length. Unless you're NEVER pulling too much but regardless, I can't see how that would be approved by code at that length. What am I missing here?
What are you missing? Probably the fact that I wasn't specific (you didn't miss anything). I never operate at the end of a 400ft. feeder trunk run... typically the 125ft. runs are the longest I use past the venue outlet. Oftentimes position one ea. spider box off to the side (or under) each side of the stage with a 50ft. feeder cable passed through the first and feeding the second... so the total feeder cable run might be a max of 175ft.
Of-course, I'd think if my 6/3 & 8/1 was undersized for code concerning the total length of run from the venue serive panel... the feeder cable AND the venue wiring would have to be up-sized to meet code.
If more amperage is needed, I'll run a second feeder cable from a second venue outlet... either that, or prune down the draw to work within that which is reasonably available.
Again, I'm a small operator in a small market... doing small-time stuff. What I run is boarderline over-kill for what I do. I'm seldom ever running anywhere near max capacity on my distros... I can oftentimes run off-a 3 or 4ea. 15 - 20A 117v "Edison" 5-15 or 5-20 outlets... but if a 14-50 is available, it's easier and less to leave to chance just running the distro, especially if power is "a-ways away".
theshow wrote:Also, why didn't you just used the same wire throughout the cable? I know I've recently read that you "can" get away with running the neutral (or is it ground) with less gauge but why do that? What's the gain other than a smidgen of weight and price? To me, the advantages don't seem worthy enough to justify going through the hassle of getting one different gauged wire compared to the other three. Of course maybe the weight and the price is significant and if so, let me know.
The basic reason is that 6/3 & 8/1 is what was commonly available for the application... most of my feeder cable I bought preassembled (slightly used) from big rental outfits. It's common off-the-shelf stuff.
That's why a drive a Chevy van too... it's common... same thing lots of folks use that do things similar to what I do.
Also, if you experience assembling the 50A 125/250v single phase twist-lock ends on cables, you find those ends are seemingly better suited (designed and built) for accomodating 6/3 & 8/1 rather than 6/4... and 4/4 is pretty-much a no-go.
01-31-2013 04:02 PM
----Miko man
OP, if you have the knowledge and experience to determine that a home-made distro meets the applicable portions of either the NEC or local electrical codes (as you imply from your comments about being sure that some are), I have no business offering my inexpert (but somewhat well-informed) comments and suggestions on how you should go about dealing with your electrical supply needs.
Best wishes in your endeavors, sir. Mark C.------
Where did I say I have the knowledge and experience to determine if a homeade distro is applicable to NEC or local electrical codes? I never implied that at all. I stated that I was getting knowledge and learning more from every post. NOT ONCE did I state or imply that I would make one or that my end result would be to have one made at this point.
Keep in mind, by using the term "homeade" I am referring to the same type of distros that we've seen 1000's upon 10's of 1000's of people use throughout the years without issue. I am not verifying that their distros were up to code or acceptable by any means because I have no idea. I am simply using "those" types of distros as a reference. A reference only.
But "homeade" in the terms of the word would imply that I myself would be making a distro and I do NOT intend, nor desire to make one on my own. I simply don't know how. So, I couldn't even if I wanted to BECAUSE I don't have that knowledge.
Why do you think I came here asking questions? To get the knowledge to have the right solution. There are many solutions to a situation. I am not looking for the solution that is neither safe or acceptable by codes. I want both of those.
And if I've said that "some" are, then I am speaking on behalf of the ones that just might be. I can't know if every single distro out there is NOT up to codes or safe. I'm sure that there are a lot that are. Again, apparently there are since they are being used every day in the 1000's. You can't tell me that 1000's of bands and production companies everyday are getting away with using homeade distros and 1000's of city inspectors across the nation are just overlooking them can you?
Don't confuse my questions with knowledge. I've never claimed to know how to buld a distro. But I do have more knowledge of how they are put together and why now. That still doesn't mean that I believe to have the knowledge of whether or not they are code applicable or safe at this point.
01-31-2013 04:08 PM
-----Road Ranger
Peavey manuals (and their website) notoriously suck. There's nothing in that distro to limit the current draw to 40A. The breaker supplying the range outlet is the limiting factor. It might have something to do with their UL certification - functionally it will make no difference. Furman doesn't have the best of reputations either but their distro is OK I think - only five 20A circuits though? Something from Motion Labs would be nice but I forget if they are UL certified - one of the big makers out there isn't and your local inspector might look for that.-------
Well, how am I supposed to know if the Peavey manual is correct or not? Sheesh, if you can't trust a manual listed by the seller and/or manufacturer themself, than who can you trust? Perhaps they didn't make the distro and just slapped their name on it but still, should I be able to trust that piece of information?
Anyway, I understand the need to get more info on that and by looking at the inside of one, it does "appear" to not have other limiting things to minimize the available amperage per side. But I don';t know really so I'm just going off of the manual.
I also agree that 5 - 20 amp circuits is limiting too. I don't know. I suppose the reality of the situation is that if I'm planning on using this for one rack and the available outlets are needed to power everything in that rack alone, then 5 or 6 - 20 amp outlets that actually end up having 10 or 12 outlets is probably plenty. Since I would be planning on 3 or 4 amps and only a couple other things, it's probably double what I need. But the Peavey has no 50 amp "pass through" or 30 amp available outlets that would be nice to have.
Yes, I want to make sure I invest in something that is acceptable by inspectors and is safe.
01-31-2013 04:11 PM
---Miko man,
I believe that Motion Labs gear is "ETL" certified, rather than UL. Whether a local inspector will accept ETL certification as readily as UL is an open question.... Mark C.----
Well, I know that will be the tricky part of the whole situation. What may be acceptable by many states may not be in a few others. Worse yet, what may be acceptable in one town, may not be acceptable in another town that I could be doing a festival for 100 or only 50 miles away. Yes, that is the crappy part.
01-31-2013 04:17 PM
---dboomer,
I can tell you as I designed it but as a former employee I am NOT speaking for Peavey nor for my current employer.
UL has an odd rule that derates the plug that is mounted on the cable to 40A ... even though it is a 50A plug. Once that plug is mounted to a cable that "cable assembly" can only be rated for 40A. Go figure???
If the box were supplied without a cable it would have carried a 50A UL rating. So each leg can distribute that "rated" 40A (if you get my drift) across 3 20A breakers to that max.
"Capable" and "rated" have different meanings
----
Very interesting. Well, I understand that you can't speak on behalf of your previous employer for liability purposes and I don't want to get into anything here but that makes for some interesting conversation.
Yes, I suppose "capable" and "rated" do indeed have different meanings. In this conversation as well, the same could be true for the phrases or words such as: "acceptable by codes" and "safe."
What one city or state may find acceptable for their code may be deemed "safe" to them and provide the adequate power necessary for a given situation and even though that same situation may be the exact same in another city or state, they may not deem it "as safe." Or, perhaps worse yet, a city inspector may deem a situation safe by their standards when in reality it is not by the reality of the situatioin. That's something to consider too.
01-31-2013 04:27 PM
---Audiophile,
I never operate at the end of a 400ft. feeder trunk run... typically the 125ft. runs are the longest I use past the venue outlet. Oftentimes position one ea. spider box off to the side (or under) each side of the stage with a 50ft. feeder cable passed through the first and feeding the second... so the total feeder cable run might be a max of 175ft.
Okay, so your comment about "400 feet" previously was regarding your "total" accumulated length of cable in multiple pieces? If so, now I got it. And I understand what you mean by using a second box 50 feet away by simply connecting from the "pass through" of the first box.
If more amperage is needed, I'll run a second feeder cable from a second venue outlet... either that, or prune down the draw to work within that which is reasonably available.
Yep, I'm sure a lot of people do that as needed. Again, site surveys are my big thing to try to get the correct information beforehand to be prepared. And if nothing else, if the place doesn't have enough power to power all the equipment I would be bringing for an event, now sense hauling all of that an unloading it and setting it up right? Just a waste if you can't use it or get out of it what you would like.
Again, I'm a small operator in a small market... doing small-time stuff. What I run is boarderline over-kill for what I do. I'm seldom ever running anywhere near max capacity on my distros... I can oftentimes run off-a 3 or 4ea. 15 - 20A 117v "Edison" 5-15 or 5-20 outlets... but if a 14-50 is available, it's easier and less to leave to chance just running the distro, especially if power is "a-ways away".
Yes, I'm small too and I've been fortunate to "get by" with using multiple outlets for many shows. However, those days are going away for some future shows that just won't get away with that type of setup. Plus, I hate running multiple extension cords.----
01-31-2013 06:27 PM
theshow wrote:
------Anyway, as far as the Peavey distro being 80 amps, that is the spec that the site gives. I know it says it has 6 available 20 amp circuits (3 - 20 amp circuits per leg as you pointed out) but according to their site, the Peavey distro is only rated for 80 amps of TOTAL load. Unless I'm reading something wrong there.
Just because they have 3 separate 20 amp circuits doesn't mean that each leg is rated for 60 amps or even 50 in our case of the discussion for 14-50R receptacles.
Actually, here are the specs from the manual:
FEATURES:
• 80A total load
• Six 20 amp circuits
• High Inrush Magnetic Circuit Breakers (Switch Grade)
• Plugs into standard NEMA 14-50 socket (Range Plug)
• Compact 2u package
When plugging in equipment, divide the load as follows: The X leg supplies circuits A,C & E while the Y leg powers circuits B, D, & F. Each leg can provide 40 amps so divide your loads so they are balanced between the legs (for example, put one subwoofer amp on each leg, not both on the same leg).
--So, if you look at that, it is ONLY capable of 40 amps per leg, NOT 50 like I would desire.--
I know we can argue whether 20 amps is a lot but that's not the point. The point is, if I'm plugging into a 14-50R receptacle, I want to take advantage of as much of that power as I can. In which case, if it's puttin out 50amps x 2 (100 amps) of available power to my distro, then I want that extra 20 amps.
Oh good f'ing grief. Remember the point about how important the details are? Here's why:
The Peavey distro is rated at 40 amps per leg continuous because of the NEC 80% derating rule for continuous loads, BUT you have to understand what the definition of a continuous load is. By the NEC, it's a lighting or motor/industrial process load that remains effectively steady state for 4 or more hours. An audio or stage lighting load (except house lighting) specifically does not fall under the continuous load derating because it's a dynamic load. same for typical stage lighting applications. UL requires a general purpose distro to be rated as a continuous load supply device because it MAY be used soe some applications in a continuous environment. Therefore, removing the NEC derating factor yields 40 amps x 1.25 = 50 amp. Yay, it's just like magic.
If you look at it, you will see that it uses 3 x 20 amps breakers per leg... now are you ready for more magic? That seems like 60 amps right? In fact, why it's allowed is for load diversity, because two breakers may have 18 amps and the third only 10 amps. That's a total load on that leg of 46 amps and A-ok. Now, if Mr. Sparky thinks he knows what he is doing but makes a calculation or judgement error and loads each 20 amp circuit with say 18 amps, that's 54 amps which after the time delay associated with the feeder breaker's inverse time curve, the feeder breaker (at the source end of your feeder protecting the 50 amp recepticle) will trip opening up both poles (legs) of your feeder (due to the common device rule).
You will not pass an inspection using 50 amp range plugs (regular 15-50's) because they are specialty listed for range and limited purpose use. Most inspectors will allow a single connection to a supplied range recepticle but no in line connectors. CA newstyle twists are what are currently considered standard for the portable power industry.
Regarding breaking up your feeder into 100' sections, IMO you would be foolish to go any longer than 100' with anything larger than #6. The weight would be a total ball buster. Obviously you have no appreciateion for the unwieldiness of what you are proposing. If you can not depend an ANYONE else, sir, you are in the wrong business and will get your ass in a serious bind at the most inopportune time. You do not know and can not appreciate what you do not know.
01-31-2013 06:31 PM
theshow wrote:---Miko man,
I believe that Motion Labs gear is "ETL" certified, rather than UL. Whether a local inspector will accept ETL certification as readily as UL is an open question.... Mark C.----
Well, I know that will be the tricky part of the whole situation. What may be acceptable by many states may not be in a few others. Worse yet, what may be acceptable in one town, may not be acceptable in another town that I could be doing a festival for 100 or only 50 miles away. Yes, that is the crappy part.
ETL is accepted in every jurisdiction the UL is accepted. Both are NRTL's and carry identical credentials when the products are tested to the same published standards. It's not crappy at all, it's part of being a big boy and putting on your big boy pants and following industry standards. Don't reinvent the wheel, I know you don't understand what I am, saying but it's the truth. Sheesh.
01-31-2013 06:41 PM - edited 01-31-2013 06:48 PM
theshow wrote:Yes, I'm small too and I've been fortunate to "get by" with using multiple outlets for many shows. However, those days are going away for some future shows that just won't get away with that type of setup. Plus, I hate running multiple extension cords.----
In a broad sense, I see the thresholds as follows:
1) you can run off-a venue "Edison" outlets: somewhere around 15amps... maybe a little more per circuit @ 117v... depending.
2) you can comfortably run off-a 14-50 outlets, which is probably the biggest bang for the buck if it's available cost per watts wise.
3) Next step up is 100 amp single phase 220V... which is cumbersome and kind of old skool for the hoops you've generally gotta jump through to graduate to this league.
4) Next step up, and is fairly common is 200 amp single phase 220V, which isn't much more cumbersome to deal with than 3) once you're set-up for it, and doesn't involve any more hoops to jump through.
5) Next step up generally gets into 3 phase 200 or 400 amp 220V stuff... similar hoops to jump through as 3) and 4), but more expensive hardware.
Point being: If you've decided that 1) is history, and have reservations that 2) might not cut the mustard for your future, skip to 4) or 5), and rethink your budget and skill set by likely two or three orders of magnitude.
01-31-2013 06:50 PM
Audiopile wrote:
theshow wrote:Yes, I'm small too and I've been fortunate to "get by" with using multiple outlets for many shows. However, those days are going away for some future shows that just won't get away with that type of setup. Plus, I hate running multiple extension cords.----
In a broad sense, I see the thresholds as follows:
1) you can run off-a venue "Edison" outlets: somewhere around 15amps... maybe a little more per circuit @ 117v... depending.
2) you can comfortably run off-a 14-50 outlets, which is probably the biggest bang for the buck if it's available cost per watts wise.
3) Next step up is 100 amp single phase 220V... which is cumbersome and kind of old skool for the hoops you've generally gotta jump through to graduate to this league.
4) Next step up, and is fairly common is 200 amp single phase 220V, which isn't much more cumbersome to deal with than 3) once you're set-up for it, and doesn't involve any more hoops to jump through.
5) Next step up generally gets into 3 phase 200 or 400 amp 220V stuff... similar hoops to jump through as 3) and 4), but more expensive hardware and much more dealing with Mr. Murphy... and all that goes with Murph's anticts.
Point being: If you've decided that 1) is history, and have reservations that 2) might not cut the mustard for your future, skip to 4) or 5), and rethink your budget and skill set by likely two or three orders of magnitude.
01-31-2013 07:05 PM
Oh good f'ing grief. Remember the point about how important the details are? Here's why:
The Peavey distro is rated at 40 amps per leg continuous because of the NEC 80% derating rule for continuous loads (Okay, I don't know where that was stated and I'm sorry if I overlooked that "detail." I wasn't trying to overlook it by any means and I may have to go back and reread some things (which I am sure I will do) but it may have got put in somewhere when discussing grounds and other things. I don't know. But I wasn't taking the derating rule into consideration. Sorry. BUT you have to understand what the definition of a continuous load is. By the NEC, it's a lighting or motor/industrial process load that remains effectively steady state for 4 or more hours. An audio or stage lighting load (except house lighting) specifically does not fall under the continuous load derating because it's a dynamic load. same for typical stage lighting applications. UL requires a general purpose distro to be rated as a continuous load supply device because it MAY be used soe some applications in a continuous environment. Therefore, removing the NEC derating factor yields 40 amps x 1.25 = 50 amp. Yay, it's just like magic.
I get it now that you consider the derating rule. But now we're into the whole thing that is similar to amps and their ratings. One amp say 2000 watts and another says 1000 watts. Which one makes more power? Well, you and I know that the 1000 watt amp could "easily" put out more power and sound better and blah blah blah. So, we're back to the rating system of things. If the Peavey distro is rated for 50 amps, then why doesn't it just say so instead of not doing it? Sheesh.....I'm just looking at it from the way they present it. I didn't get into considering the other factors. Thanks for clearing that up.
If you look at it, you will see that it uses 3 x 20 amps breakers per leg... now are you ready for more magic? That seems like 60 amps right? In fact, why it's allowed is for load diversity, because two breakers may have 18 amps and the third only 10 amps. That's a total load on that leg of 46 amps and A-ok. Now, if Mr. Sparky thinks he knows what he is doing but makes a calculation or judgement error and loads each 20 amp circuit with say 18 amps, that's 54 amps which after the time delay associated with the feeder breaker's inverse time curve, the feeder breaker (at the source end of your feeder protecting the 50 amp recepticle) will trip opening up both poles (legs) of your feeder (due to the common device rule).
I understand this and know this. It wasn't magic, it was math and the way loads are dispursed. But I get that. But up until recently, nobody informed me that each "leg" would be good with 46 amps each. I was under the impression that the distro could only handle 50 amps "total" due to the plug. But now that I have more knowledge and understanding, I know that not to be the case. Again, learning.
You will not pass an inspection using 50 amp range plugs (regular 15-50's) because they are specialty listed for range and limited purpose use. Most inspectors will allow a single connection to a supplied range recepticle but no in line connectors. CA newstyle twists are what are currently considered standard for the portable power industry.
Again why I would rather stay away from extension cords (larger feeder cords) if at all possible. Just more to hassle with in the way of additional plugs and protecting them from the elements and people and keeping them safe and within code.
Regarding breaking up your feeder into 100' sections, IMO you would be foolish to go any longer than 100' with anything larger than #6. The weight would be a total ball buster. Yes, I know this already. I've carried them and yes, they aren't light. Obviously you have no appreciateion for the unwieldiness of what you are proposing. How do you know I have no appreciation for things? Please don't claim to know something that you don't, it's very unfair. Being willing to do something that I don't like (hauling around heavy things) and appreciating them are two completely different things. Furthermore, you have no idea if I can lift heavy things or not. Or if my setup crew can.
f you can not depend an ANYONE else, sir, you are in the wrong business and will get your ass in a serious bind at the most inopportune time. I have people that setup larger events with me as needed. For smaller ones, I take care of what I need to. The point about my comment of relying or depending on other people is because the bottom line is: you can't always depend on other people to do the things you need. Sure, we can hire 20 techs or load crew but getting all 20 to show up may be a different story. In which case, am I suppose to stop the show because 1 or 2 didn't show up? You know that's not the case. So, my point about having people to rely on was simply to be prepared to do things yourself. In which case, I do try to do as much as I can to minimize risk. When you rely too heavily on other people, you do have added risk and I doubt you will disagree with that.
A smart man (Warren Buffett) has a billboard with a saying that to me makes a lot of sense. It says: "Invest in yourself."
Pretty much sums up a lot of things. I'm considering all of this (these questions and responses) an investment and I sincerely appreciate all of the wisdom and knowledge I've gained from them. Don't confuse my remarks as anything other than "appreciation" please.
You do not know and can not appreciate what you do not know
(see above)
01-31-2013 07:06 PM
BTW: Two 12ga. extension cords roughly = 1 ea. 10ga. extension cord.
01-31-2013 07:15 PM
Aged,
ETL is accepted in every jurisdiction the UL is accepted. Both are NRTL's and carry identical credentials when the products are tested to the same published standards. It's not crappy at all, it's part of being a big boy and putting on your big boy pants and following industry standards. Don't reinvent the wheel, I know you don't understand what I am, saying but it's the truth. Sheesh.
Aged, thanks for clerifying whether or not ETL is acceptable in every jurisdiction that UL is. The comment about "being crappy" has nothing to do with the products and how they're tested. You misunderstood my comment regarding that. The reference to "crappy" had nothing to do with that and had to do with the fact that yes, one city inspector may accept something that a different city inspector may not just down the road. Heck, even in the same city there are different electrical inspectors for each zone and even they could have a way of looking at things differently. Sure, the "idea" is to get consistency but as we all know, that's not that case.
Hence why EVERY single person mentions to get things approved by the city or area you're doing your event at. Because they know that things can be different from one are to the next.
And THAT IS crappy.
THAT has nothing to do with putting on big boy pants and you misunderstood my comment competely. Where in the world did I say or imply that I want to reinvent the wheel here? Asking questions to understand a situation is FAR from reinventing the wheel. It's simply trying to get a better understanding about things.
Actually Aged, I do understand exactly what you're saying on many of your comments. And with each new post, I gain a better understanding. And I appreciate the input. Just don't confuse what you are misunderstanding about my comments and questions to be anything different than what they are. But you are doing that so please understand what my comments mean.
01-31-2013 07:20 PM
Audiopile,
In a broad sense, I see the thresholds as follows:
1) you can run off-a venue "Edison" outlets: somewhere around 15amps... maybe a little more per circuit @ 117v... depending.
2) you can comfortably run off-a 14-50 outlets, which is probably the biggest bang for the buck if it's available cost per watts wise.
3) Next step up is 100 amp single phase 220V... which is cumbersome and kind of old skool for the hoops you've generally gotta jump through to graduate to this league.
4) Next step up, and is fairly common is 200 amp single phase 220V, which isn't much more cumbersome to deal with than 3) once you're set-up for it, and doesn't involve any more hoops to jump through.
5) Next step up generally gets into 3 phase 200 or 400 amp 220V stuff... similar hoops to jump through as 3) and 4), but more expensive hardware.
Point being: If you've decided that 1) is history, and have reservations that 2) might not cut the mustard for your future, skip to 4) or 5), and rethink your budget and skill set by likely two or three orders of magnitude.
At this point, obviously 1 is still doable in a lot of cases. #2 would be probably where I'm at right now. For option #3, I don't know if you're referring to 240 volt 50 amp service (which would be 100 amps total and what we've been discussing here) or something else. If it is something different, then no, I'm probably not looking for that option at this point. As for step 4 or 5, I am NOT wanting to go to that level at this point.
I'm simply referring to a very common use of the 14-50R plugs at many venues nationwide. From there, anything lower I can take care of. Anything higher and yes, we're talking about something different. And NO, I don't want to understand that right now.
Baby steps right?
01-31-2013 07:27 PM
01-31-2013 07:34 PM
theshow wrote:Audiopile,
In a broad sense, I see the thresholds as follows:
1) you can run off-a venue "Edison" outlets: somewhere around 15amps... maybe a little more per circuit @ 117v... depending.
2) you can comfortably run off-a 14-50 outlets, which is probably the biggest bang for the buck if it's available cost per watts wise.
3) Next step up is 100 amp single phase 220V... which is cumbersome and kind of old skool for the hoops you've generally gotta jump through to graduate to this league.
4) Next step up, and is fairly common is 200 amp single phase 220V, which isn't much more cumbersome to deal with than 3) once you're set-up for it, and doesn't involve any more hoops to jump through.
5) Next step up generally gets into 3 phase 200 or 400 amp 220V stuff... similar hoops to jump through as 3) and 4), but more expensive hardware.
Point being: If you've decided that 1) is history, and have reservations that 2) might not cut the mustard for your future, skip to 4) or 5), and rethink your budget and skill set by likely two or three orders of magnitude.
For option #3, I don't know if you're referring to 240 volt 50 amp service (which would be 100 amps total and what we've been discussing here) or something else. If it is something different, then no, I'm probably not looking for that option at this point.
What I meant to say is likely what I said concerning option #3. 220V 100A service yields 200A @117V.
If you've gotta push the envelope concerning option #2... jump to option #4 or #5 as #4 or #5 is not all that more cumbersome or hoop involved as #3... go past #2 and things get expensive... similar orders of magnitude as graduating from #1 to #2. If you think you need to figure out a way to stuff a #3 basketball down a #2 sized hose... well... the #4 hose works and isn't all that more involved than the #3 hose.
01-31-2013 07:36 PM
RoadRanger wrote:Are we havin' fun yet?
Actually "yea".
Where's your sporting spirit?
01-31-2013 07:42 PM
01-31-2013 07:50 PM
RoadRanger wrote:Oh, and I did mention option #2.5 - run two range plug distros. I've seen two outlets in a couple different venues.
Really? Do you work around these parts?
I ask because I've paid for the installation of... oh... I dunno... multiple dozens of R14-15's installed at area venues over the past couple decades locally... so I can run my distros... and typically I pay to install 2 at a time (because it doesn't generally cost all that much more than paying to install one).
Or maybe there's others elsewhere who have figured this out... and you've been fortunated enough to drive on the road they paved?